TonyW":2e36i7nc said:I also think that the actual lights may need to have a fire rating - assuming there is a habitable room above the kitchen.
haggisbasher":2wpgriks said:floors in multi storey houses need 30min fire resistance from below even if its your house above, therefore fire rated spots or intumescent hoods are required.
ECA":2wpgriks said:Do I need to install fire hoods/fire rated downlighters in every situation?
It really depends on whether the ceiling forms part of a fire compartmention, its construction and if it has been specified by the client/contract.
Generally speaking, a dwelling is considered to be a single compartment with regards to fire (Part B of the Building Regulations), unless it has an integral garage or has a floor that is above 4.5 m from the ground (3-storey). In the case of 3-storey dwellings, fire protection should be fitted to downlighters between the upper 2 floors unless the first and second floors are served by a protected stairway leading to two fire separated routes on the ground floor or directly to an exit door (no fire separating floors in this situation).
Where recessed downlighters are installed in ceilings that are not fire compartments such as the intermediate floor of a 2-storey dwelling, the ceiling needs to have a minimum fire rating of 30 minutes.
Research was commissioned in 1996 to look into the effect on the fire resistance of plasterboard ceilings with conventional rectangular joists having recessed downlighters installed (with no boxing in or fire hoods). The results of the tests were published in the July 1996 edition of Building Control Magazine. These results confirmed that downlighters, even without being boxed in and with no fire hoods in plasterboard ceilings, have little significant effect on fire resistance ratings up to 30 minutes. It must be inferred from these tests, therefore, that at least with plasterboard ceilings with conventional rectangular joists, it is not necessary to 'box in' downlighters or to use fire hoods for the purpose of restoring the fire resistance capability of ceilings that are not of fire compartment construction.
The definition of a FSE according to the approved doc is:7.2":261bx801 said:If a fire-separating element is to be effective, then every joint, or imperfection of fit, or opening to allow services to pass through the element, should be adequately protected by sealing or fire-stopping so that the fire resistance of the element is not impaired
The approved document gives the requirements for a compartment wall/floor as:Fire-separating element":261bx801 said:A compartment wall, compartment floor, cavity barrier and construction enclosing a protected escape route and/or a place of special fire hazard.
This fits in exactly with the quote I gave earlier and Section 7.4 backs this up in a round about way by stating:Compartment walls/floors":261bx801 said:Compartment walls and compartment floors should be provided in the circumatances described below...
5.3: Every wall separating semi-detached houses, or houses in terraces, should be constructed as a compartment wall and the houses should be considered as separate buildings.
5.4: If a domestic garage is attached to (or forms an integral part of) a dwellinghouse, the garage should be separated from the rest of the dwellinghouse.
As proven during the tests mentioned in my last post, downlighters do not impair the fire rating of a ceiling sufficiently for the use of a fire rated spot to be required. This does not mean it is wrong to do so just that it is not a requirement to do so in ceilings within the same dwelling.7.4":261bx801 said:For instance, where downlighters, loudspeakers and other electrical accessories are installed, additional protection may be required to maintain the integrity of a wall or floor.
haggisbasher":o0w0z56a said:I was just trying to head it off in case it was headed toward something less civilised.
Fire Rated Downlights & the Building Regulations in the UK
Document B, England & Wales; Technical Handbook No:2, Scotland; and Technical Booklet E, Northern Ireland
Demands that if a fire resistant element e.g. a ceiling protecting an upper floor, is broken into to install services, such as recessed spotlights, the fire resistance must be made good. The recent Approved Document P makes specific reference to the electrician's responsibility to ensure that the fire resistance of any floor, ceiling or wall that any services he has installed pass through, are properly re-instated, with possible legal consequences for non-compliance.
IEE Wiring Regulations 16th Edition BS 7671:2001, section 527-02-01 reinforces this same stance, and this applies to all buildings:
“Where a wiring system passes through elements of a building construction...the openings remaining...shall be sealed according to the degree of fire resistance required of the element concerned...”
Thanks for that - more what I was after, however interesting the debate on fireproofingMisterfish":sfexrcjx said:Lots of good stuff
haggisbasher":mpa0db01 said:Dave
The fire resistance is to make sure that the floor remains a floor for, in this case 30 minutes. a floor must maintain the ability to carry its loads for 30mins under test and maintain its integrity i.e. not permit passage of smoke or fumes. These terms are from the BS fire tests and fire testing has three elements Loadbearing, Integrity and Insulation.
The reason that fire doors are not required in 2 storey houses is that it is considered that people can escape from first floor rooms by getting out of windows. Therefore the stair doesn't need protecting. Once you go to 3 storeys you need fire doors because you cant jump from the second floor( bearing in mind this is reasonable theory not what would you do if your house was on fire) and the only way out is back down the stair.
The reason that the ceiling/ floor needs protection is simply due to the dynamics of fire. Fires grow vertically, they emit smoke that builds up layers at the ceiling until that smoke reaches the critical temperature at which time it ignites in what is called a flashover. Even if you leave your doors open the ceiling will be at a temp of over 1000 degrees in minutes probably before the smoke reaches your nearest smoke detector.
Tom
The BS7671 quote is accurate, but the issue that is still cloudy for me (and every spark I have spoken to) is whether a 65mm hole with a metal downlighter fitted will actually reduce the fire resistance of the ceiling below the 30 minute requirement - all the info I have read so far says that they do not, but I look forward to reading the BRE report, I checked their website but they don't have any downlighter tests on there.Fire Rated Downlights & the Building Regulations in the UK
Most downlighters require a hole less than half the size mentioned. The majority of the ones I have fitted required a 65mm hole.In general, normal 240v recessed downlighters (normally about 140mm in diameter) have not been found to be problematical where there use is restricted to 3 or 4 units placed a reasonable distance apart.
I heard that BRE did a similar test that came to the same conclusion but it could be my memory playing up and it was in fact BSI. Perhaps though the BRE redid the test and found conflicting info which is what you have read more recently?we have an old document lying in the office citing a 1996 BSI test on fire resistance of ceilings fitted with downlights.
their findings....
due to the construction of the fitting, glass and metal, the ceilings passed their tests, so generally we dont fit hoods unless we are told to and then price accordingly....
No problem - it's the nature of internet fora and adds to the group knowledge anyway.davy_owen_88":286lc70g said:I too apologise for going on about this Pete.
They look like just what I'm after - thanksIf I can offer one bit of advice it would be not to buy hoods and buy fire rated downlighters such as these.