I think I've got a leak in the coil of my hot water tank.

So this afternoon I've disconnected the coil from the heating system, capped it and pressure tested it.

In 3 hours the gauge has dropped from 40 psi to 34 psi and is still dropping.

Am I right to think it's knackered?

sasha
 

Dibs-h

Established Member
Joined
23 Jul 2007
Messages
4,207
Reaction score
1
Location
West Yorkshire
When you say disconnected it - I assume you've disconnected both ends of they as the enter\exit the tank, etc.?

In which a pressure loss would mean knackered tank to me.

HIH

Dibs
 

Doug B

Shy Tot
Joined
6 Aug 2008
Messages
2,898
Reaction score
82
Location
@dougsworkshop
You could always un-cap both ends & put a tub/bucket under the bottom tapping of the coil, if it fills with water you have a leaky coil.
They usually go with a pin hole forming in the coil & the give away signs are that the central heating header tank starts over flowing as the bigger domestic hot water header tank is usually higher & the water is trying to find its own level.

HTH.

Cheers.

Edit, depending on how you`ve capped the ends you could be getting a pressure drop as some plumbing fittings aren`t air tight
 

9fingers

Established Member
Joined
26 Jul 2005
Messages
5,000
Reaction score
0
Location
Romsey, Hampshire
Also your coil is full of air surrounded by a water jacket and the water temperature could be falling during your test?

pressure is proportional to absolute temperature (kelvin)

Bob
 