Hi everyone,
I'm looking for some advice on a problem with our oil boiler system.
We have a self-build with a new condensing oil boiler from Elco Klockner and underfloor heating. It is feed by through a glass viewing filter in turn fed by a lifting pump / reservoir (not air tight sealed). Externally there is a fire cutout valve. The pipe to the tank is approx 50m and the boiler is 1m higher than the tank outlet. The pipe is 8mm plastic coated copper and runs underground in a black duct. We've a high water table, so any crack in the ducting means there is a good chance the pipe is sitting in water.
Every few months, the boiler starts stopping, and my perception is its more so in colder & wet weather. Also, it 'seems' to stop more at the weekends, when the only difference in that room I can think of is that the Washing Machine / Tumble dryer are running more. The heating / water programme is the same.
There is no evidence of air bubbles / condensation / dirt in the filter. Also, apart from one time when the tank emptied, the filter vessel has not run dry, ie oil appears to be available to the boiler. I've asked the oil supplier is they've had any bad batches - again no problem.
Elco have been out several times under warranty.
On the first visit, the filter in the burner nozzle was blackened, and they replaced. They also replaced the boiler oil pump as it was broken.
2nd visit replaced the complete burner assembly, again, nozzle black, and it worked well for a few months after that. On a the main boiler burner.
3rd visit, new nozzle filter, has worked well over the summer till now, when over the last few weeks its began stopping lots - eg Sunday 10 times. Only once per day Mon & Tues.
Anyway, Elco and the builder say the problem lies with the supply pipe / pump /tank install, not the boiler. Tank / pipe installer says boiler problem not pipe. Me, I'm stuck in the middle surrounded by 'experts' who don't know what to do next.
I was wondering if anyone had any ideas - could the oil be too cold / viscous into the boiler, could the boiler be susceptible to room temp / humidity. What sort of things could cause the blackening of the nozzle filter.
Any thoughts / help much appreciated.
Could anyone recommend a good oil engineer in the Reading area?
I'm looking for some advice on a problem with our oil boiler system.
We have a self-build with a new condensing oil boiler from Elco Klockner and underfloor heating. It is feed by through a glass viewing filter in turn fed by a lifting pump / reservoir (not air tight sealed). Externally there is a fire cutout valve. The pipe to the tank is approx 50m and the boiler is 1m higher than the tank outlet. The pipe is 8mm plastic coated copper and runs underground in a black duct. We've a high water table, so any crack in the ducting means there is a good chance the pipe is sitting in water.
Every few months, the boiler starts stopping, and my perception is its more so in colder & wet weather. Also, it 'seems' to stop more at the weekends, when the only difference in that room I can think of is that the Washing Machine / Tumble dryer are running more. The heating / water programme is the same.
There is no evidence of air bubbles / condensation / dirt in the filter. Also, apart from one time when the tank emptied, the filter vessel has not run dry, ie oil appears to be available to the boiler. I've asked the oil supplier is they've had any bad batches - again no problem.
Elco have been out several times under warranty.
On the first visit, the filter in the burner nozzle was blackened, and they replaced. They also replaced the boiler oil pump as it was broken.
2nd visit replaced the complete burner assembly, again, nozzle black, and it worked well for a few months after that. On a the main boiler burner.
3rd visit, new nozzle filter, has worked well over the summer till now, when over the last few weeks its began stopping lots - eg Sunday 10 times. Only once per day Mon & Tues.
Anyway, Elco and the builder say the problem lies with the supply pipe / pump /tank install, not the boiler. Tank / pipe installer says boiler problem not pipe. Me, I'm stuck in the middle surrounded by 'experts' who don't know what to do next.
I was wondering if anyone had any ideas - could the oil be too cold / viscous into the boiler, could the boiler be susceptible to room temp / humidity. What sort of things could cause the blackening of the nozzle filter.
Any thoughts / help much appreciated.
Could anyone recommend a good oil engineer in the Reading area?