....Probably a silly question from a newbie, but should an NVR switch on a bandsaw buzz when the machine is switched off?
It doesn't always and if you wiggle the buttons it comes and goes.
...
I have a NVR type unit from an Austrian piece of equipment that hums/buzzes whenever there is mains power supplied to it.
The holding solenoid is permanently powered via the Stop (Push to break) Button and in its rest (no mechanical load) position against the solenoid core the armature buzzes.
The Power to Device (output) contacts are made by the On Button which mechanically latches contacts to the armature when actuated.
Hit the Stop Button or switch off power at source and the Mechanical Latch of the On Button contacts is released, opening up the output contacts. The design of the On button is such that it has to be physically returned to OFF before it will engage the output contacts again, an alternate to having a mechanical latch on the Stop Button.
Rather a poor design, saves on a set of coil contacts but means that if power is not isolated at source the coil in the NVR is subject to mains power and attendant heating and a possible out of hours fire risk if you don't isolate shop power.
So basically in answer to your question is yes they can, dependant on design, but not the Norm for the majority of units where the holding coil is only powered when you push the start button.
Does your Bandsaw have a rotary On Switch that latches On, could be indicative of a unit with permanently powered coil as above.