OLD
Established Member
My suggestion protects the swa cable yours keeps lights etc on when house rcd trips .Note shed rcd trips at lower current than house so no interaction.Above is covered by discuss with sparks or is this a diy.
Jake":2bkrxi36 said:flying haggis":2bkrxi36 said:garywayne":2bkrxi36 said:I am going by what I have read.
"Armoured cable is expensive and has to be terminated at a special junction box at each end of its run, where it can be joined to ordinary PVC-insulated cable".
not true
What are you saying is not true?
waterproof junction boxes on the outside wall to connect the T&E to the SWA.
SemiSkilled":3ikxfjfa said:waterproof junction boxes on the outside wall to connect the T&E to the SWA.
Why d'you want to connect t&e to the swa?
jlawrence":tenv0uix said:I've read that bit about less than 50mm depth needing RCD protection.
My sparky said that they almost never put lighting circuits on the RCD side.
If the 50mm depth is completely correct (I'm not saying it isn't), then every circuit in a dwelling would need RCD protection. EVERY single circuit in a house is at somepoint not buried 50mm deep - take the point at which it connects to a socket or lighting point for example.
When I replace my connection to the workshop I won't be taking it from the RCD side. Like others I don't want the lights going out if (when) I trip something in the workshop - either that or I'm going to need to look at putting an emergency light in (which may not be a bad idea really).
jlawrence":2ijvd99h said:I've read that bit about less than 50mm depth needing RCD protection.
If the 50mm depth is completely correct (I'm not saying it isn't), then every circuit in a dwelling would need RCD protection. EVERY single circuit in a house is at somepoint not buried 50mm deep - take the point at which it connects to a socket or lighting point for example.
matt":3lzy2eei said:I don't get why you'd NOT want to use RCD protection for a cable carrying a high current on a high AMP fuse in a potentially vulnerable route.
DavidE":3d719i35 said:matt":3d719i35 said:I don't get why you'd NOT want to use RCD protection for a cable carrying a high current on a high AMP fuse in a potentially vulnerable route.
Just for background infomation on what RCDs are used for...
RCDs primarily provide shock protection for humans/livestock who come into contact with the live whilst earthed. There are also used to provide fault protection should an earth fault occur on a circuit where the fuse would not blow within the stated disconnection time. This is mainly for the sake of shock from the raised voltage on the earth of the circuit and the potential fire risk.
Therefore, the size of cable and current don't really come into it. If you touch a live wire whilst earthed no fuse is going to help you. The RCDs on sockets typically trip at 30mA very quickly. A fuse won't have even blinked with that current going through you - hence why the cable/fuse size doesn't come into it.
I hope this is useful - you can get breakers called RCBOs which incorporate overload protetcion too which leads to the confusion about the purpose of an RCD.
David
Would that be a reasonable interpretation?I don't get why you'd NOT want to use RCD protection for a cable in a potentially vulnerable route.
I'm not really sure I understand what you just said but if I had said:
I don't get why you'd NOT want to use RCD protection for a cable in a potentially vulnerable route.Would that be a reasonable interpretation?
Enter your email address to join: