This John Ward video covers earthing outbuildings pretty well:
If it’s twin and earth, the earth is smaller than the other two, e.g. for 2.5mm2 T&E, the earth is 1.5mm2.At the moment the power circuit in my workshop is in 2.5mm and the lighting circuit in 1.5mm. The earthing circuits are therefore in 2.5 and 1.5 mm cable.
You have stated an obvious potential problem, if that existing 10 mm2 pvc is say T&E then the conductors may be 10mm but the CPC will not. Now without extranous parts the bonding issue goes away but changing the size of the CPC is not good practice. Solution would be to run just a two core live & neutral and use earth rod at the workshop which covers everything, even if you do have extranous parts. Make sure the armour is earthed but only at the workshop end. As I have mentioned in another post the dangers stem not from yourself but at the supply with a PME system. If the Neutral fails at the supply side then you lose Neutral and Earth but still have live. Now if there is a load connected, it obviously will not work but it will mean the Neutral is now also LIVE, ( look at Ohms law) and with extranous conductive parts that are connected to Earth they will also become live, so you have a hazard. With an Earth rod this will prevent conductive parts having a higher potential than ground/Earth and so reduces the hazard of touch/step voltages.Unless John Ward is wrong then there seems to be nothing to prevent the use of 3 core 10 mm2 armoured cable connected to the existing 3 core 10 mm2 pvc cable already wired into my CU by an electrician.