Trench for water, electricty and waste

UKworkshop.co.uk

Help Support UKworkshop.co.uk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Molynoox

Established Member
Joined
17 Jan 2021
Messages
985
Reaction score
703
Location
Billericay
Hi All,

I am making progress with my garden room build, groundscrews have been installed and I have now started digging the trench.
The below is my current trench 'design' if you can call it that - there doesn't seem to be any clear answers on the topic of combining all 4 types of service in one trench
I have kept to 100mm spacing between the services
I may use conduits for all or some, not sure on that - maybe electricity and comms in one conduit?
I have placed water as far away from waste as I can, to avoid contamination in case of a leak, but not sure if this is really going to help or is necessary (I did read somewhere that this was advisable, but I am not sure how the waste could enter the water pipe, but anyway)

your thoughts on this?

thanks
Martin

Trench design.jpg
 
It might be useful to see my overall plan for the trench position also, see pic.
The run is about 10 - 15 metres long

Services 3.jpg
 
Having a nice conversation with myself here :-D just modified my design so uploading the latest.

Trench design 2.jpg
 
When i did mine( no waste pipe) I put them all in one trench inside 2 drainage pipes which come up flush to the inside wall and are capped flush to the floor. Easy to pull through extra cables if needed.
Having just seen the added picture it might be a better idea if you do two trenches 1 for the waste and the other for whats left ,that way you avoid those bends which could cause a problem if you need to pull through another cable .
 
Something’s ringing a bell in my head, to not put the Wi-Fi too close to the mains, or was that hi-fi?
Sorry not to be of more help. Ian
 
It's great that you're thinking about this now instead of a few years from now if something has to change. I've done dozens of renovation and construction projects in Europe that involve adding utilities and communications where none existed or the existing infrastructure was inadequate.

Paying for the trench or hole in the ground tends the be the most expensive part of the project and is an event we tried to do only once for the expected life of the facility. Since you are working with distances of about 15 meters, you can easily incorporate suitable ducting in the trench that can make your shed future-proof for changes in technology or maintenance.

Keep the bends in the ducting to a minimum so pulling cable in the future will be easier. The more bends you have, the more opportunities you create for the cables to bind or break. You can never have too many pull stings in conduit. It is much better to have five unused pull strings than to need one that doesn't exist.

Keep power and communications separate. Even with fiber cable, it is standard practice here to keep power and comms separate.

Give consideration to the utilities that could fail in the future and will need access from the surface. If everything is layered in one trench, what will you not want to dig past to access what is below it? With a restriction of one trench, I would put the comms on the bottom in a suitably sized duct. We use 100mm round duct that has four internal round ducts to create separate ducts for the different communications cables. This is overkill for a residential application, but if the cost is reasonable, I would use this and install pull strings in each duct during the installation. This reduces the likelihood of a new cable snagging on existing cable later.

Make sure you use the appropriate warning tape for each utility that is placed in the trench as it is filled. This tape follows the path of the associated utility and is the first warning anyone digging in the area will see before reaching the pipe, cable, or duct buried beneath it. This is especially important for direct burial cable.

Document the location of the trench using reference points from several fixed points, such as corners of permanent structures. We use at least two reference points for several points along the path, each junction, or each bend. If the trench is straight with no junctions in the buried conduit, then we document a point one meter from each point where it enters the buildings, as well as the middle. The documentation also includes the depth below grade of the top of the conduit, pipe, or cable. This is easy to do before the trench is covered and will save lots of time later if you have to access something years from now. Based on your drawing, you have at least five permanent reference points that can be used to pinpoint any location to millimeter accuracy along the path of the ducting. Adding photos of the trenching to the documentation is also a good idea.
 
Your trench depth could be dictated by the waste pipe depending on the fall and don't forget to fit a roding point, might be easier to just put this in it's own trench first along with the water and then you can keep the other trench dead straight looking at your drawing. Now all you need is a duct, soil pipe is not the cheapest but probably the easiest or rain / gutter pipe but brown underground soil is cheaper and run the Two core armoured through this with a screened and armoured data cable, or just a screened data cable depending on the type of data link and router location. Mike has made some good points about warning tape above the ducts and keeping a record of where you put it.
 
Don't forget that building regs apply to the depth, fall, bedding, jointing and inspection arrangements for the foul drainage - can't remomber which approved doc it is. Where the water pipe goes from internal to external and vice versa I'd do pipe in pipe to ease installation and protect it - you've obviously spotted that it needs to be 750 deep min to protect from frost - I'd put an isolation valve outside the new build in a suitable chamber. Wiring regs apply to the type and installation method for power - I'd consult a spark to make sure that you choose the correct type of SWA cable and installation methods (the workshop may or may not also require its own earth rod, depending on what the spark recommends). I agree with the idea of putting a separate conduit for data cable, with a pulling rope installed before you bury it.
PS building regs may also require you to have an SVP or a durgo valve at the upstream end
 
A quick google for 'combined service trench detail uk' brings up a lot of results. There is a lot of good advice regarding spacing.
 
This is the standard for under a U.K. pavement, not sure if building control would insist on this for a home building, worth asking as they’ll want to inspect the drains.

190BE3A7-41C6-472D-AFDC-3EA0BADAF463.jpeg
 
Digital photography is free at point of use, I always take loads of photos of any hidden stuff now, really useful when you come back to it years later. Copy on hard drive and well orderd copy on a USB stick in the house file box.

If you use ducts maybe leave a pull through line in it, who knows what you might want in future. Mains coffee from a machine in the house? Steam pipe for cappuccino making....
 
Electrical supply to the outbuilding depends upon the type of supply to the property which determines the means of earthing. Best leave this to the sparky doing the design and install.
 
When i did mine( no waste pipe) I put them all in one trench inside 2 drainage pipes which come up flush to the inside wall and are capped flush to the floor. Easy to pull through extra cables if needed.
Having just seen the added picture it might be a better idea if you do two trenches 1 for the waste and the other for whats left ,that way you avoid those bends which could cause a problem if you need to pull through another cable .
don't suppose you have any pictures of that conduit arrangement?
 
It's great that you're thinking about this now instead of a few years from now if something has to change. I've done dozens of renovation and construction projects in Europe that involve adding utilities and communications where none existed or the existing infrastructure was inadequate.

Paying for the trench or hole in the ground tends the be the most expensive part of the project and is an event we tried to do only once for the expected life of the facility. Since you are working with distances of about 15 meters, you can easily incorporate suitable ducting in the trench that can make your shed future-proof for changes in technology or maintenance.

Keep the bends in the ducting to a minimum so pulling cable in the future will be easier. The more bends you have, the more opportunities you create for the cables to bind or break. You can never have too many pull stings in conduit. It is much better to have five unused pull strings than to need one that doesn't exist.

Keep power and communications separate. Even with fiber cable, it is standard practice here to keep power and comms separate.

Give consideration to the utilities that could fail in the future and will need access from the surface. If everything is layered in one trench, what will you not want to dig past to access what is below it? With a restriction of one trench, I would put the comms on the bottom in a suitably sized duct. We use 100mm round duct that has four internal round ducts to create separate ducts for the different communications cables. This is overkill for a residential application, but if the cost is reasonable, I would use this and install pull strings in each duct during the installation. This reduces the likelihood of a new cable snagging on existing cable later.

Make sure you use the appropriate warning tape for each utility that is placed in the trench as it is filled. This tape follows the path of the associated utility and is the first warning anyone digging in the area will see before reaching the pipe, cable, or duct buried beneath it. This is especially important for direct burial cable.

Document the location of the trench using reference points from several fixed points, such as corners of permanent structures. We use at least two reference points for several points along the path, each junction, or each bend. If the trench is straight with no junctions in the buried conduit, then we document a point one meter from each point where it enters the buildings, as well as the middle. The documentation also includes the depth below grade of the top of the conduit, pipe, or cable. This is easy to do before the trench is covered and will save lots of time later if you have to access something years from now. Based on your drawing, you have at least five permanent reference points that can be used to pinpoint any location to millimeter accuracy along the path of the ducting. Adding photos of the trenching to the documentation is also a good idea.
wow, thanks for the detail! excellent info.
 
Your trench depth could be dictated by the waste pipe depending on the fall and don't forget to fit a roding point, might be easier to just put this in it's own trench first along with the water and then you can keep the other trench dead straight looking at your drawing. Now all you need is a duct, soil pipe is not the cheapest but probably the easiest or rain / gutter pipe but brown underground soil is cheaper and run the Two core armoured through this with a screened and armoured data cable, or just a screened data cable depending on the type of data link and router location. Mike has made some good points about warning tape above the ducts and keeping a record of where you put it.

I admit I dont know what a rodding point is, but presumably it is someplace to access the drain to unblock it? I have a drain / manhole cover in the garden so I'm guessing that will do?

interesting you say about using screened comms cable and combining with electricty in same conduit - that is opposite of what others are saying. I guess if its screened comms cable though it should be fine.
 
It really depends what the cable is carrying as far as signal. If the power cable is armoured that provides a reasonable level of screening that will reduce radiated EMC, and an armoured screened shielded CAT6 cable will protect from susceptance to EMC. Coms cables using twisted pairs like CAT 5,6 etc also reduce common mode issues.

Have you thought about just using ethernet over power adaptors for the internet connection rather than cable?
 
A quick google for 'combined service trench detail uk' brings up a lot of results. There is a lot of good advice regarding spacing.

I'm not so sure about that - all the searches I did returned advice about under pavement services, not gardens, and also none of them talked about combining waste with other services. Maybe its my searching that is off.
 
Back
Top