A machine with this specification:
Voltage 1 phase + N + Earth 230V /50/60 Hz
Motor rating 1.5Kw
Motor full load current in amps 1 PH 9.0A
Starting current in amps 1 PH 56.0A
Required fuse size in amps 1 PH 25A
Required cable size 1PH 2.5mm
Can one use some type of phase, invertor, stepper transformer to run the machine safely off a 230 volt domestic supply?
 

lurker

Le dullard de la commune
Joined
2 Mar 2007
Messages
5,576
Reaction score
180
Location
Leicestershire
Unless I am missing something, it's just plug and go off a normal 3 pin plug.

Edit: just spotted the required fuse size. Seems a big start surge to me?
 

mhannah

Established Member
Joined
23 Feb 2004
Messages
46
Reaction score
0
Location
Glasgow
According to the 13a fuse characteristics graph, a 13A fuse could withstand a 56A load for about 6 seconds.
 

sunnybob

wysiwyg
Joined
11 Oct 2014
Messages
8,399
Reaction score
162
Location
cyprus
Thats a heavy motor! Exactly what is it running?
Your problem is whats known as "start up voltage" which is the "kick" the motor needs to start turning.
This can be overcome with capacitors and accommodated with slow burn fuses, but its not the way it should be done.

The correct way is to have a dedicated cable from your consumer unit, with a 32 amp MCB and a wall terminal with a cooker type socket for it to be hard wired in.

Always consult a local electrician in unusual circumstances.
(or read the instructions of course :lol: :lol: )
 

sunnybob

wysiwyg
Joined
11 Oct 2014
Messages
8,399
Reaction score
162
Location
cyprus
The only correct way of installing it is with a dedicated line on its own mcb and hard wired into a wall socket.
Everything else is iffy.
 

Trevanion

Greatest Of All Time
Joined
29 Jul 2018
Messages
3,775
Reaction score
572
Location
Pembrokeshire
No electrician, but a single-phase PT255 with a 1.5KW motor should borderline run off a regular 13A plug as I've seen many with a regular 13A plug on, but really they should have a 16A OR 32A plug on or be wired direct.

I think the numbers in the newer manuals is buttocks-covering more than anything. "Did you wire it properly into a supply exceeding 25A? Then that's your problem" etc... I've got a couple of 2.2KW machines that run fine off a 16A plug and a couple of 1.5KW machines that run fine off a regular 13A house plug, never been an issue.

So long as you're quoting the right information of course and haven't picked up the single-phase specifications by accident when you meant to post the three-phase spec.
 

sunnybob

wysiwyg
Joined
11 Oct 2014
Messages
8,399
Reaction score
162
Location
cyprus
The other problem here is the length of cable involved. If this is in a shed at the bottom of the garden running off an extension lead, its going to trip the fuse every single time.
If the consumer unit isnt in the same building its not going to work off a 13 amp supply.
 

ManowarDave

Fighting the World
Joined
31 Jul 2018
Messages
97
Reaction score
38
Location
Worcester
Hi,

As sunnybob said, you should install to a separate MCB on the consumer unit. Make sure it is a type D (also known as d curve). These are designed for loads with high in rush current such as motors.

From consumer unit to double pole isolator then 16A (blue) socket.

Dave
 

sunnybob

wysiwyg
Joined
11 Oct 2014
Messages
8,399
Reaction score
162
Location
cyprus
Dave, as you say, a blue socket single phase is 16 amp.
The spec requires a 25 amp fuse. That would lead to overheating of the plug / socket over time.
hard wired would be best case.
 

ManowarDave

Fighting the World
Joined
31 Jul 2018
Messages
97
Reaction score
38
Location
Worcester
Hi sonny,

Agreed on hard wired. Missed the 25A fuse rating. However given the characteristics of the type D MCBs and the continuous current rating of the motor, I'd put it on a 16A MCB.

Dave
 

pollys13

Established Member
Joined
19 Apr 2009
Messages
1,176
Reaction score
0
Location
Swindon
Trevanion - yes was correct spec for a single phase machine, manual does say not to run on a 13 amp socket.

sunnybob - The correct way is to have a dedicated cable from your consumer unit, with a 32 amp MCB and a wall terminal with a cooker type socket for it to be hard wired in.
Yes I'll go down that route, wouldn't want something to go pear shaped, then trouble with the insurance man :)
Thanks everyone else for chipping in..... sorry :)
 

Trevanion

Greatest Of All Time
Joined
29 Jul 2018
Messages
3,775
Reaction score
572
Location
Pembrokeshire
After having a think about it I realised why there’s such a large start amperage specified, there’s two motors in the machine which I had totally overlooked and forgotten about. There’s the 1.5kw cutterblock motor but there’s also the motor for the powerfeed. Which if memory serves is about 0.5kw. But I believe on the single-phase machines they’re on separate switches so it’s not one massive power drain trying to start two motors at the same time from the same supply.
 

Sideways

Established Member
Joined
26 Dec 2017
Messages
1,255
Reaction score
199
Location
United Kingdom
PT255 - the little 10" wide one, is a single motor unit. Feed rollers are continuously driven from the spindle drive via a flat belt and spring loaded pulley before you get to the chain drive.
PT's have a fair weight to spin up in the block and feed rollers so no surprise that the startup surge runs towards the higher end: 6-7x full load current. I've metered the startup on a similar size axminster trade machine and they pull 50 odd amps for a couple of seconds too before dropping back to about 7A at idle.
I'm absolutely not saying that you should, but a machine of this size will run off a 13A plug. It is also so close to the limit of a 13A fuse that it ages them and you could be replacing the fuse every few weeks.
Admittedly not having done the time / current / heating calcs but for a full load current of 9A, I would expect a relatively small machine like this to run fine off a 16A circuit wired in 4mm to a type C MCB.
I bought one. That's what I plugged it into. It ran fine, but the motor was worn so it's part stripped pending a refurb. I didn't bother doing any further measurements.
The machine is protected by a thermal overload relay in it's starter. It will take no harm from being plugged into a higher capacity circuit than it needs.
 

RogerS

Established Member
Joined
20 Feb 2004
Messages
17,391
Reaction score
78
Location
In the eternally wet North
sunnybob":1ceg6uvr said:
The other problem here is the length of cable involved. If this is in a shed at the bottom of the garden running off an extension lead, its going to trip the fuse every single time.
If the consumer unit isnt in the same building its not going to work off a 13 amp supply.
You seem to have a 'thing' about extension cables as you've now posted twice " its going to trip the fuse every single time.". I also asked for clarification on this in the other thread but you may have missed it.

Why " its going to trip the fuse every single time."
 

sunnybob

wysiwyg
Joined
11 Oct 2014
Messages
8,399
Reaction score
162
Location
cyprus
Have you never tried to work something that has a high start up on the end of an extension lead? it will trip (sorry Doug).

try an arc welder on a 30 metre lead. I have seen iron nails squeezed into 13 amp plugs to keep them going. 2.5 mm cable forced into 13 amp plugs because the 1.5 mm "keeps smoking".
I have seen so many real life "in front of my eyes" scary occurances that I base all of my advice on my experience.
I once got called to a shop that had just been rewired and found an appliance catch fire as I was working on it, because the cable had been installed by an electrician who thought he could save a couple quid by downsizing .
Theory is great in the classroom, but working with less than 100% efficient machines in less than 100% perfect environments causes problems that never should happen on paper.
 

RogerS

Established Member
Joined
20 Feb 2004
Messages
17,391
Reaction score
78
Location
In the eternally wet North
sunnybob":1xdaca1i said:
....
Theory is great in the classroom,...
Yes. A knowledge of Ohm's Law would be appreciated.

If I understand you correctly, you're saying that plug an arc welder into a 13amp socket on the wall and it's fine. But plug in an extension cable to feed the arc welder and the fuse blows ? Which fuse? The one at the end of the arc welder cable or the one at the end of the extension cable ?
 

Distinterior

Established Member
Joined
8 Mar 2014
Messages
835
Reaction score
129
Location
Colchester, Essex.
Following on from Sunnybob's point....

A good mate of mine decided to buy a tall electric Patio Heater for use in the evenings on the cooler summers evenings.
Until he bought this new heater, he had been using as Calor Gas version...

He paid A LOT OF MONEY for this new heater and the first time he used it, we were all round his house for an evening BBQ.

The heater seemed to be doing the job and it was all turned on and working as we arrived.
After about 5 mins, I could smell that odour that comes from electric cables getting hot, so I turned round to see the domestic extension lead still coiled up in its plastic drum and the 13A plug plugged into it.....smoking away..!!! I immediately turned it off. There was nearly as much heat coming from the extension lead as was being generated from the heater itself....

The flex cable that came as standard on the heater was a 2.5mm CSA but was only about 2 mtrs long, not quite long enough to reach the socket in the Dining Room through the Patio Doors, so my mate just thought to plug it into an extension lead but only un coiled about another 2 mtrs. The rest of the extension lead was still coiled up.....and it was only 1.5mm CSA.....

I checked the specifications of the heater and it had a total load of 4500W....
I think the heater was made in Italy if I remember correctly.
 