DrPhill":31qmktw5 said:
..... Since mine is on a 40 amp breaker, and the sparks would have made sure that the breaker protected the wiring does (how do you know that to be the case ? ) that mean that I am good to go with the upgrade from 8. to 9.5kw? ....

...
 

Racers

Established Member
Joined
22 Apr 2005
Messages
9,172
Reaction score
127
DrPhill":2pc7zlk0 said:
I never thought of the tolerance in the supply. I wonder what guarantees the power company give?

230 volts
In the UK, the declared voltage and tolerance for an electricity supply is 230 volts -6%, +10%. This gives an allowed voltage range of 216.2 volts to 253.0 volts.

Pete
 

DrPhill

Cyber Heretic
Joined
15 Feb 2012
Messages
964
Reaction score
83
Location
West Somerset
RogerS":3prnjf5z said:
DrPhill":3prnjf5z said:
..... Since mine is on a 40 amp breaker, and the sparks would have made sure that the breaker protected the wiring does (how do you know that to be the case ? ) that mean that I am good to go with the upgrade from 8. to 9.5kw? ....

...

I guess that that is an assumption, but it was all part of the same job - the consumer unit (and choice of breaker) was installed to supply the shower, and the wiring to the bathroom (including fan/switches etc) was all installed new at the same time. Would that be an unsafe assumption? If so I could begin to doubt every aspect of the job..... :D
 

DrPhill

Cyber Heretic
Joined
15 Feb 2012
Messages
964
Reaction score
83
Location
West Somerset
Racers":285e3ph8 said:
DrPhill":285e3ph8 said:
I never thought of the tolerance in the supply. I wonder what guarantees the power company give?

230 volts
In the UK, the declared voltage and tolerance for an electricity supply is 230 volts -6%, +10%. This gives an allowed voltage range of 216.2 volts to 253.0 volts.

Pete

Thanks. Can we hold them to it?
 

RogerS

Established Member
Joined
20 Feb 2004
Messages
17,390
Reaction score
79
Location
In the eternally wet North
DrPhill":3g0xdnqd said:
RogerS":3g0xdnqd said:
DrPhill":3g0xdnqd said:
..... Since mine is on a 40 amp breaker, and the sparks would have made sure that the breaker protected the wiring does (how do you know that to be the case ? ) that mean that I am good to go with the upgrade from 8. to 9.5kw? ....

...

I guess that that is an assumption, but it was all part of the same job - the consumer unit (and choice of breaker) was installed to supply the shower, and the wiring to the bathroom (including fan/switches etc) was all installed new at the same time. Would that be an unsafe assumption? If so I could begin to doubt every aspect of the job..... :D

Can you not see what size/type of cable is there coming out of the consumer unit or is it all hidden away ? If it were me then I'd be taking off the front cover of the CU and having a decko at the cable.
 

Jake

Established Member
Joined
5 Apr 2004
Messages
5,584
Reaction score
233
Location
London
The difference between 6mm and 10mm is pretty obvious if you have seen both before, but if not... The cable clips often have the size on them. The earth conductor will be a giveaway too if you take the CU cover off, 6mm being single solid core, 10mm being stranded.
 

DrPhill

Cyber Heretic
Joined
15 Feb 2012
Messages
964
Reaction score
83
Location
West Somerset
Thanks Jake - there is a picture (several posts back) of the cable just before it enters the bathroom, complete with tape measure. Does that identify the cable?
 

Jake

Established Member
Joined
5 Apr 2004
Messages
5,584
Reaction score
233
Location
London
I'm not going to guess from a photo. If I were you I'd take the front off the CU carefully (it's safe as long as you don't touch anything) and have a look at the earth wire. All of the earth wires from all of the wires in the CU will all go to one or two banks of earth terminals at the top of the CU like this:

url


You should be able to see which comes from your cable and it'll be obvious enough if it is stranded or not.

aclk


or 6mm solid earth

aclk


This is all obviously just to give you a steer on what the sparks will say when he has a look at the installation as a whole and nothing more.
 

DrPhill

Cyber Heretic
Joined
15 Feb 2012
Messages
964
Reaction score
83
Location
West Somerset
Plumber has just been and wont change the spec without say so from a qualified electrician - so what I think/find wont matter :cry:

So its 8.5kw and no 50 gbp saving.

But thanks for the advice and pictures.
 

Terry - Somerset

Established Member
Joined
22 Dec 2012
Messages
1,171
Reaction score
601
Location
Taunton
Somewhat cynically I suspect 8.5kw showers were originally installed as they were confident this would be ok with a smaller size of cable. Overall probably a cheaper installation!

Go up to 9.5kw and the cable becomes marginal - although it seems to depend partly on the length of the cable and how it is routed.

Shower manufacturers know this. I don't expect there is much difference in manufacturing cost between an 8.5 and 9.5kw unit, but for the punter the difference is often the extra cost of new cable installation by a qualified electrician.

£10-50 extra cost on the shower unit is trivial compared to the labour, material and disruption cost of re-cabling!
 

Racers

Established Member
Joined
22 Apr 2005
Messages
9,172
Reaction score
127
DrPhill":1t9tf7jn said:
Racers":1t9tf7jn said:
DrPhill":1t9tf7jn said:
I never thought of the tolerance in the supply. I wonder what guarantees the power company give?

230 volts
In the UK, the declared voltage and tolerance for an electricity supply is 230 volts -6%, +10%. This gives an allowed voltage range of 216.2 volts to 253.0 volts.

Pete

Thanks. Can we hold them to it?

They changed the tolerance to allow us to keep the same voltage (240V) and harmonize with Europe (230V)

Pete
 

Racers

Established Member
Joined
22 Apr 2005
Messages
9,172
Reaction score
127
Don't forget that the length of cable affects the size of the cable, you need a bigger cable for long runs.

Pete
 

HappyHacker

Established Member
Joined
1 Jan 2016
Messages
448
Reaction score
44
Location
Chester
DrPhill":1s9pozge said:
Racers":1s9pozge said:
DrPhill":1s9pozge said:
I never thought of the tolerance in the supply. I wonder what guarantees the power company give?

230 volts
In the UK, the declared voltage and tolerance for an electricity supply is 230 volts -6%, +10%. This gives an allowed voltage range of 216.2 volts to 253.0 volts.

Pete

Thanks. Can we hold them to it?

In theory yes, in practice unlikely.
I was at a customers and the supply voltage was 190V at 18:00 but was OK during the day. Tested with two calibrated meters. I told the customer to phone their supplier and complain.

I saw the customer a few months later, they had complained and were fobbed off. I would have phoned myself but the customers parents both had problems and having me working in the house was a problem so I had to work quickly and get out and she did not want to get me involved.

Apparently it took them forever to cook Christmas dinner when all their neighbours were trying to do the same.
 