Ceiling rose to flush fitting- help needed

UKworkshop.co.uk

Help Support UKworkshop.co.uk:

stuckinthemud

Established Member
Joined
17 Jun 2019
Messages
303
Reaction score
142
Location
Caerphilly
I need to swap my standard loop--in ceiling rose for a flush fit (new, non-pendant light fitting), I'm not a sparks, but the advice the guy in the shop gave me to swap the ceiling rose for a multiblock connector doesn't feel right. Any advice? Getting in a professional has already been blocked by household accounts dept...
20210529_172116.jpg
 

Cabinetman

Established Member
Joined
5 Jan 2017
Messages
2,380
Reaction score
1,249
Location
lincolnshire Wolds
Not sure exactly what it is you’re trying to change it to, so it depends how much weight is going to be hanging, from what really. The electrics on what you’ve shown is relatively simple there are three brass connector strips which you could replicate with a chocolate block as I called them and shove it back up into the ceiling, as I said it depends what it is you’re hanging from it and how much it weighs, you may need to go in the attic and put a noggin across between the joists although it’s quite probable that there is already one there. Ian
 

Ollie78

Established Member
Joined
4 Aug 2011
Messages
1,071
Reaction score
441
Location
Wiltshire
Get some wago connectors (I used 221`s )and a wago box enclosure. These are very simple to use and the boxes are safe to be left in voids etc.
Replicate the wiring of the ceiling rose inside the box thus preserving the switched live etc. Run the positive and negative (the brown and blue in your example) to your new light fitting.
The box can be put inside the loft or floor void etc.

Did pretty much the whole house this way when we changed to all led fittings.

Ollie
 

flying haggis

Established Member
Joined
7 Mar 2009
Messages
1,387
Reaction score
681
Location
norfolk
using choc block and tape in the ceiling void is not really the best way. a proper junction box like this is much better

from the pic do you have two way switching for the light? as you seem to have a conductor missing. again from the pic wagos in box might be better
 
Last edited:

stuckinthemud

Established Member
Joined
17 Jun 2019
Messages
303
Reaction score
142
Location
Caerphilly
Thanks all. Wago clips look way easier than choc blocks! It's just a single switch, I'd disconnected the earth before I thought to take a photo. Its a downstairs light so I fastened to a ceiling joist. There's a bit of filling required to make good where the rose was but in the end I went with the choc blocks as that is what I had to hand, definitely going to buy a bag of wagos though.
 

pe2dave

Established Member
Joined
2 Oct 2007
Messages
1,242
Reaction score
352
Location
Peterborough, Cambs, UK
Agree with @Ollie78 - but first, check how much room you have above the plaster? Then make as big a hole as you can get away with, bearing in mind your new 'flush' fitting needs something to screw into? Wego without a box, if room as tight.
 

NetBlindPaul

Established Member
Joined
23 Jun 2009
Messages
319
Reaction score
62
Location
South Wales
For information, as the job is completed by the sound of things.
“Chock block” connectors “stuffed” in the ceiling void, is not compliant with BS7671.
I understand that you are doing this as a DIY job, but, you need to realise that your insurance company will have expectations within the small print of your policy, and you still have a legal obligation to comply with the building regulations.
Guidance document P refers, and whilst the work might not be notifiable, it is not absolved from comply.
Wago connectors (other brands are available, as long as they are compliant), & a suitable maintenance free junction box (has to be designated as such to be compliant) would meet the requirements of BS 7671, & thus building regulations.
Therefore it should meet any insurance policy requirements, providing you have test documents to comply with the requirements of BS 7671 to prove that the circuit is still sound following the modification.
 

pe2dave

Established Member
Joined
2 Oct 2007
Messages
1,242
Reaction score
352
Location
Peterborough, Cambs, UK
Therefore it should meet any insurance policy requirements, providing you have test documents to comply with the requirements of BS 7671 to prove that the circuit is still sound following the modification.

Am I right in thinking that after any change to wiring an inspection is required? Is this for *most* household buildings insurance?
I had a new dist board installed and the entire house was inspected / tested / errors (from builders) corrected. Not quite an arm
and leg, but close.
 

stuckinthemud

Established Member
Joined
17 Jun 2019
Messages
303
Reaction score
142
Location
Caerphilly
NetBlindPaul, thankyou, I had a strong feeling multiblock connectors were not compliant, hence the question, if I know my better half, the fitting won't be up long and I'll replace with wagos
 

Stevekane

Established Member
Joined
24 Feb 2018
Messages
287
Reaction score
101
Location
Nr Bournemouth
I realise this is a minefield but,,where is the switched live in the picture getting its power from? Could it be from a multiway switch perhaps? Only asking as I like to feel I sort of understand these things,,
Steve.
 

Stevekane

Established Member
Joined
24 Feb 2018
Messages
287
Reaction score
101
Location
Nr Bournemouth
Hi Dave and many thanks, however try as I might I cannot see the 3rd live that I expected in the photo, usual thing is a bunch of 3 “reds” but there is only two shown I think, the 3rd red shown is you would expect the switched live,,,so where is it getting its power from?
Steve
 

pe2dave

Established Member
Joined
2 Oct 2007
Messages
1,242
Reaction score
352
Location
Peterborough, Cambs, UK
Hi Dave and many thanks, however try as I might I cannot see the 3rd live that I expected in the photo, usual thing is a bunch of 3 “reds” but there is only two shown I think, the 3rd red shown is you would expect the switched live,,,so where is it getting its power from?
Steve
Does it not match up to the circuit at Ceiling rose wiring (older cable colours) ?
Normally, switched live is via the switch? Mains lighting ring, via switch, to light socket?
You don't say (or I missed it) if it is single switch, or double (top and bottom of stairs for example).
 

GuitardoctorW7

Established Member
Joined
14 Jul 2019
Messages
50
Reaction score
34
Location
London
Get some wago connectors (I used 221`s )and a wago box enclosure. These are very simple to use and the boxes are safe to be left in voids etc.
Replicate the wiring of the ceiling rose inside the box thus preserving the switched live etc. Run the positive and negative (the brown and blue in your example) to your new light fitting.
The box can be put inside the loft or floor void etc.

Did pretty much the whole house this way when we changed to all led fittings.

Ollie
Yep, what he said. Just started using them excellent product
 

NetBlindPaul

Established Member
Joined
23 Jun 2009
Messages
319
Reaction score
62
Location
South Wales
Am I right in thinking that after any change to wiring an inspection is required? Is this for *most* household buildings insurance?
I had a new dist board installed and the entire house was inspected / tested / errors (from builders) corrected. Not quite an arm
and leg, but close.
The requirements for insp and testing are within the British Standard, this document is referenced in the Approved Document (P) for compliance with the Building Regulations.
The onus is on the person undertaking the work to inspect and test, complying with the requirements of BS 7671.
The onus for compliance with Building Regulations is on the property owner. (There might be slight differences in the wording and responsibility across the whole spectrum of property).
The requirements are that the work is safe and compliant with the requirements and that it can be demonstrated, by, for example, suitable certification as required by BS 7671.
 