Established Member
As far as I am aware correctly rated and fitted junction boxes are perfectly acceptable and unless "part P" has changed, the fitting of a few sockets into and existing ring main is still not notifyable work as long as carried out by a competent person and therefore does not require a certificate.
The following types of work are non-notifiable:
Replacing accessories such as socket-outlets, control switches and ceiling roses
Replacing the cable for a single circuit only, where damaged, for example, by fire, rodent or impact (1)
Re-fixing or replacing the enclosures of existing installation components (2)
Providing mechanical protection to existing fixed installations (3)
Installing or upgrading main or supplementary equipotential bonding (4)
Work that is not in a kitchen or special location and does not involve a special installation (5) and consists of:
- adding lighting points (light fittings and switches) to an existing circuit (6)
- adding socket-outlets and fused spurs to an existing ring or radial circuit (6)
Notes:
(1) On condition that the replacement cable has the same current-carrying capacity, follows the same route and does not serve more than one sub-circuit through a distribution board;
(2) If the circuit's protective measures are unaffected;
(3) If the circuit's protective measures and current-carrying capacity of conductors are unaffected by increased thermal insulation;
(4) Such work shall comply with other applicable legislation, such as the Gas Safety (Installation and Use) Regulations;
(5) Special locations and installations are listed below;
(6) Only if the existing circuit protective device is suitable and provides protection for the modified circuit, and other relevant safety provisions are satisfactory.
The following types of work are non-notifiable:
Replacing accessories such as socket-outlets, control switches and ceiling roses
Replacing the cable for a single circuit only, where damaged, for example, by fire, rodent or impact (1)
Re-fixing or replacing the enclosures of existing installation components (2)
Providing mechanical protection to existing fixed installations (3)
Installing or upgrading main or supplementary equipotential bonding (4)
Work that is not in a kitchen or special location and does not involve a special installation (5) and consists of:
- adding lighting points (light fittings and switches) to an existing circuit (6)
- adding socket-outlets and fused spurs to an existing ring or radial circuit (6)
Notes:
(1) On condition that the replacement cable has the same current-carrying capacity, follows the same route and does not serve more than one sub-circuit through a distribution board;
(2) If the circuit's protective measures are unaffected;
(3) If the circuit's protective measures and current-carrying capacity of conductors are unaffected by increased thermal insulation;
(4) Such work shall comply with other applicable legislation, such as the Gas Safety (Installation and Use) Regulations;
(5) Special locations and installations are listed below;
(6) Only if the existing circuit protective device is suitable and provides protection for the modified circuit, and other relevant safety provisions are satisfactory.