OK
I'm afraid that this is rather a complicated area - hope the following is not too over-the-top
Electricity in England is generated as 3-phase. Each phase changes its voltage amplitude in time in a sinewave pattern and the amplitude at a given time can be described by the following equation
V*Sin(omega * t) + phi where omega is 2 *pi*f (f= frequency = 50Hz), t is time and phi is the phase angle
A single waveform will curve up from zero V to fully positive V, down to zero V again and then down to fully negative V and up again to zero V in a given time and this is defind as one cycle
Mains electricity in UK has
50 cycles per second (Hz)). Each cycle is defined as a rotation of 2*pi radians which is
360 degrees.
For three phase, we generate 3 of these sinewave voltages at
120 degrees apart, thus, for example, the first (red phase) will pass through zero V at
0 degrees, the second sinewave (blue phase) will pass through zero for the first time at
120 degrees and the third sinewave (yellow phase) will pass through zero V at
240 degrees.
Three phase waveforms looks like this:
(any one of these plus a neutral is the the supply you get in your house) E is the voltage amplitude and for English distribution system would be 586.81 V peak (415V RMS)
All three phases are sent out to the sub stations. What the electricity board do is take a different (single) phase (Red, Blue or Yellow) + a neutral to each street and then to each house in that street. Phases are generally not mixed in a street and so all will be on red or all on yellow etc.
The
240 V you know and love is the RMS voltage between a single phase and Neutral
(RMS = Root Mean Squared = SQRT((Peak V * Peak V)/2)
Between ANY two phases we get an
RMS voltage of 415V. When all three phases are joined at the power station, the mid point = ZERO V and is the Neutral that you use in your house.
3-phase has a higher voltage and can deliver more power to a machine (there are other advantages, particularly for motor design but that's enough for now)
I will try to post some pictures tonight to clarify a little